This manual describes how to remotely change settings in our MultiPlusses, MultiGrid, MultiPlus-II, Quattros and high power Inverters; all power products with a VE.Bus communication port. A feature called Remote VEConfigure
This functionality requires a GX device (Cerbo GX, or other) to be installed locally on the system.
Requirements:
A GX Device running Venus
OS v2.17 or later (latest official version is preferred)
System must connected to internet and communicating to the VRM Portal.
Two way communication must be enabled
The
GX device must be powered directly from the battery. So do not power it an AC adapter on the AC output of the inverter/charger.
Details:
Remote VEConfigure works for both single unit systems as parallel and three phase systems.
Remotely changing Assistant configuration is possible.
VE.Bus firmware versions 416 and 417 can not be configured remotely
Remote configuring firmware version 418 or later requires the GX device to run v2.10 or later
To Remote VEConfigure a system connected to the GX device via a VE.Bus to VE.Can interface, as was done in old Hub-1 systems, this interface cable needs to run firmware version v2.05 or higher. If necessary, first update that interface cable with the
Remote firmware update feature.
This (new) way of Remote VEConfigure replaces the previous mechanism, that used VE.Power Setup. See
here for the manual of the old procedure. Note that, once updated to the new Venus version, it is no longer possible to use the old procedure.
The system protects against accidentally sending settings from one system to another. To that purpose, it will compare the serial numbers of the installed inverter/chargers against the serial numbers in the configuration files. There is one exception:
For systems consisting of multiple inverter/chargers, it is possible to replace a unit without having to do a full reconfiguration: step (1) make sure to, after commissioning a new system, always make and have a .rvsc file on archive. step (2) in case a unit failed, replace that by a new one. step (3) update the new unit to the same firmware version as the rest of the system. A full archive of older firmware versions is
available here. step (4) open that old .rvsc file and use the VRM Remote VEConfigure write settings feature to send that archived configuration. While writing the settings, the mechanism accepts up to one exchanged serial number and will automatically and silently take care of that. Note that in case you don’t have a file on archive, try to make a backup before taking the failed unit out of the system. In many cases a failed unit can still communicate. This feature requires Venus
OS v2.62 or later to be installed on the GX device.
In some cases the VE.Bus system will momentarily switched off when changing the configuration.
Many settings can be changed without resulting in a shutdown during the re-configuration. Some settings though, such as a changed Assistants configuration, will cause the inverter/charger to momentarily switch off and back on again. In such situations, VEConfig will warn when saving the settings:
known issue: Venus versions v2.23 and below always reset the Multi when the following settings are changed.
Battery Capacity
Start and stop limits for low power AES mode
State of charge when Bulk finished (only resets with Multi firmware versions < 200)
Depending on how the internet communication equipment (ie. router) is powered, the internet connection might also be temporarily lost at that time.
This is not a problem, as the file is first uploaded to the GX device, and only once received and verified it will be written to the VE.Bus system.