ac_coupling:start
ac_coupling:start [2014-07-25 23:45] – Page moved from ac_coupled_pv:start to ac_coupling:start mvader | ac_coupling:start [2022-04-12 06:47] (current) – [1.1 What is AC-coupling?] bob | ||
- | ====== | + | ====== AC-coupling |
- | ===== AC Coupling | + | ===== 1. Introduction to the AC-Coupling |
- | [TODO: explain | + | Already familiar with the concepts of AC-coupling and regulating PV inverter output |
- | ===== What is frequency shifting? ===== | + | - [[:ac_coupling: |
- | [TODO: what is it? what is the purpose of it? how can a VE.Bus product configured to do it? | + | - [[:ac_coupling: |
- | From most advised to least advised: | + | - [[: |
- | - With the Self-consumption Hub-2 v3 assistant | + | |
- | - Use the Inverter period time settings on the Virtual switch tab.] | + | |
- | ===== Factor 1.0 rule: Max PV power in combination with frequency shift ===== | ||
- | ==== Rule definition | + | ==== 1.1 What is AC-coupling? |
- | In both grid-connected and off-grid systems with PV inverters installed on the output of a Multi, Inverter or Quattro, there is a maximum of PV power that can be installed. This limit is called the factor 1.0 rule: 3.000 VA Multi = 3.000 Wp installed solar power. So for a 8.000 VA Quattro the maximum is 8.000 Wp, for two paralleled 8000 VA Quattros the maximum is 16.000 Wp, etcetera. | + | |
- | ==== Example and background ==== | + | {{: |
+ | In an AC-coupled system, a grid-tied PV inverter is connected to the output of a Multi, Inverter or Quattro. PV power is first used to power the loads, then to charge the battery, and any excess PV power can be fed back to the grid. | ||
+ | When the Multi or Quattro is connected to the grid, this excess PV inverter power will automatically be fed back to the grid. | ||
+ | When the Multi or Quattro is operating in inverter-mode, | ||
+ | Highlights: | ||
+ | * AC-coupling is available in single-phase, | ||
+ | * Victron Multis and Quattros can prevent feeding back PV power to grid. | ||
+ | * Systems with only a grid-tied PV inverter will fail when there is a grid black-out. A micro-grid system will continue to operate, and even keep using solar power. | ||
+ | * It is also possible to run a AC-coupled micro-grid on a generator | ||
+ | * Most brands of PV inverters can be used for these systems, they need to be setup to support frequency shifting, often called the island-mode or micro-grid mode. For SolarEdge settings, see [[venus-os: | ||
+ | * To read out SMA inverters, see [[ccgx: | ||
+ | * If power will be fed back into the grid an anti-islanding device may have to be added to the system, depending on local regulations. | ||
+ | ==== 1.2 What is frequency shifting? ==== | ||
+ | Frequency shifting is used to regulate the output power of a Grid-tie PV Inverter, or Grid-tie Wind inverter, by changing the frequency of the AC. The MultiPlus (or Quattro) will automatically control the frequency to prevent over charging the battery. See also the chapter ' | ||
+ | For how to configure, see chapter 4. | ||
+ | ===== 2. The Factor 1.0 rule ===== | ||
+ | **The max PV power must be equal or less than the VA rating of the inverter/ | ||
+ | ==== 2.1 Rule definition ==== | ||
+ | In both grid-connected and off-grid systems with PV inverters installed on the output of a Multi, Inverter or Quattro, there is a maximum of PV power that can be installed. This limit is called the __factor 1.0 rule__: 3.000 VA Multi >= 3.000 Wp installed solar power. So for a 8.000 VA Quattro the maximum is 8.000 Wp, for two paralleled 8000 VA Quattros the maximum is 16.000 Wp, etc. | ||
+ | ==== 2.2 Example and background ==== | ||
To understand the background, consider the following situation: the PV inverter is at full power, supplying a big load. The Multi is in inverter mode. Then, suddenly and at once, this load is switched off. At that moment the PV inverter will continue operating at full power until the AC frequency has been increased. Increasing this frequency will take a very short time, but during that time all power will be directed into the batteries as there is no other place for it to go. This causes the following: | To understand the background, consider the following situation: the PV inverter is at full power, supplying a big load. The Multi is in inverter mode. Then, suddenly and at once, this load is switched off. At that moment the PV inverter will continue operating at full power until the AC frequency has been increased. Increasing this frequency will take a very short time, but during that time all power will be directed into the batteries as there is no other place for it to go. This causes the following: | ||
* When batteries are (nearly) full, the battery voltage will spike, possibly causing the Multi to switch off in DC over-voltage alarm. | * When batteries are (nearly) full, the battery voltage will spike, possibly causing the Multi to switch off in DC over-voltage alarm. | ||
Line 25: | Line 50: | ||
It is no problem to overpower the grid inverter by installing more solar panels. Some people do this to increase the generated solar power in winter time or rainy weather. Refer to the PV Inverter datasheet to maximum allowed installed PV power. Two times the inverter nameplate rating or even more is not uncommon! | It is no problem to overpower the grid inverter by installing more solar panels. Some people do this to increase the generated solar power in winter time or rainy weather. Refer to the PV Inverter datasheet to maximum allowed installed PV power. Two times the inverter nameplate rating or even more is not uncommon! | ||
- | ==== Charge current limit ==== | + | ==== 2.3 Charge current limit ==== |
- | Another question frequently asked is how can this factor be 1.0? Since the charger inside a 3000 VA Multi is not 3000 VA but closer to 2000 VA? The explanation lies in the fact that it will regulate . In other words: when there is too much power coming in, causing the charge current to exceed the limit, it will increase the output frequency again and will keep regulating the AC output frequency to charge with the limit. | + | |
+ | Another question frequently asked is how can this factor be 1.0? Since the charger inside a 3000 VA Multi is not 3000 VA but closer to 2000 VA? The explanation lies in the fact that it will regulate. In other words: when there is too much power coming in, causing the charge current to exceed the limit, it will increase the output frequency again and will keep regulating the AC output frequency to charge with the limit. | ||
- When the Multi is connected to the grid, all 3000 W can be fed back to the grid through the Multi, no problem. | - When the Multi is connected to the grid, all 3000 W can be fed back to the grid through the Multi, no problem. | ||
- In case the Multi is not connected to the grid, the 3000 Wp is more than the charger in a Multi 3000 VA can handle. The charger is around 2000 W. Therefore the grid inverter assistant will automatically increase the frequency to reduce the output of the grid inverter, to match maximum charge current. | - In case the Multi is not connected to the grid, the 3000 Wp is more than the charger in a Multi 3000 VA can handle. The charger is around 2000 W. Therefore the grid inverter assistant will automatically increase the frequency to reduce the output of the grid inverter, to match maximum charge current. | ||
- | ==== Should you look at the total PV array, or the PV inverter rating? ==== | + | ==== 2.4 Should you look at the total PV array, or the PV inverter rating? ==== |
- | The mentioned 3000 Wp and 8000 Wp is the Watt-peak which can be expected from the solar system. So for and oversized PV array, where the total Watt-peak installed PV panels exceeds the power of the PV Inverter, you take the Wp from the inverter. For example 7000 Wp of solar panels installed, with an 6000 Watt PV grid inverter, the figure to be used in the calculations is 6000 Wp. | + | |
+ | The mentioned 3000 Wp and 8000 Wp is the Watt-peak which can be expected from the solar system. So for an oversized PV array, where the total Watt-peak installed PV panels exceeds the power of the PV Inverter, you take the Wp from the inverter. For example 7000 Wp of solar panels installed, with an 6000 Watt PV grid inverter, the figure to be used in the calculations is 6000 Wp. | ||
+ | ===== 3. Minimum battery capacity ===== | ||
+ | Besides the relation between installed PV Power and the inverter/ | ||
+ | Note that, besides the minimum battery capacity, the mentioned sizes are often also the most economical battery size. In case used for self-consumption purposes that is. In case the goal is to increase autonomy, of course installing a large battery increases the system autonomy in case of a grid failure. | ||
+ | ==== 3.1 Lead batteries ==== | ||
+ | 1 kWp installed PV power requires approximately 5kWh of lead acid battery: | ||
+ | * 100 Ah at 48 Vdc | ||
+ | * 200 Ah at 24 Vdc | ||
+ | * 400 Ah at 12 Vdc | ||
+ | Each additional 1 kWp of AC PV will require an additional proportional 5 kWh increase in lead acid battery storage. | ||
+ | ==== 3.2 Lithium batteries ==== | ||
+ | 1,5 kWp installed AC PV power requires 4.8 kWh of battery storage: | ||
+ | Each additional 1.5 kWp of AC PV will require an additional proportional 4.8 kWh increase in battery storage. | ||
+ | ===== 4 Requirement of adding DC-Coupling - MPPT Solar Chargers ===== | ||
+ | Not required for Energy Storage Systems in Germany or other reliable grid situations. | ||
+ | Required for offgrid systems as well as backup systems that need to overcome extended grid failures. | ||
+ | Reason: recover from deadlock situation of AC-Coupling only situation. | ||
+ | There is no Factor 1.0 limit that applies for DC coupled PV through a Victron MPPT. Nor is there a specific minimum amount of battery storage capacity, though please follow battery manufacture specifications for maximum charge rates. A rule of thumb is C10 (10% of Ah capacity in A) for lead acid batteries, and C2 (50% of Ah capacity in A) for lithium batteries. | ||
+ | ===== 5 Software configuration ===== | ||
+ | Multis and Quattros with factory settings will not shift the AC output frequency to regulate charge current. When setting up an AC Coupled system, install either the [[ess: | ||
+ | The Inverter RS will automatically shift frequency without any additional configuration required when a surplus/ | ||
+ | Other options, __all deprecated__, | ||
+ | - Self-consumption Hub-2 v3 assistant | ||
+ | - Hub-4 Assistant in combination with the PV Inverter support Assistant | ||
+ | - Use the Inverter period time settings on the Virtual switch tab. | ||
+ | See [[https:// | ||
ac_coupling/start.1406324730.txt.gz · Last modified: 2014-07-25 23:45 by mvader
