ac_coupling:start
ac_coupling:start [2019-10-01 12:51] – guy_stewart | ac_coupling:start [2022-04-12 06:47] (current) – [1.1 What is AC-coupling?] bob | ||
Line 24: | Line 24: | ||
+ | * To read out SMA inverters, see [[ccgx: | ||
Line 38: | Line 39: | ||
**The max PV power must be equal or less than the VA rating of the inverter/ | **The max PV power must be equal or less than the VA rating of the inverter/ | ||
- | In both grid-connected and off-grid systems with PV inverters installed on the output of a Multi, Inverter or Quattro, there is a maximum of PV power that can be installed. This limit is called the __factor 1.0 rule__: 3.000 VA Multi = 3.000 Wp installed solar power. So for a 8.000 VA Quattro the maximum is 8.000 Wp, for two paralleled 8000 VA Quattros the maximum is 16.000 Wp, etc. | + | In both grid-connected and off-grid systems with PV inverters installed on the output of a Multi, Inverter or Quattro, there is a maximum of PV power that can be installed. This limit is called the __factor 1.0 rule__: 3.000 VA Multi >= 3.000 Wp installed solar power. So for a 8.000 VA Quattro the maximum is 8.000 Wp, for two paralleled 8000 VA Quattros the maximum is 16.000 Wp, etc. |
Line 51: | Line 52: | ||
Line 60: | Line 61: | ||
Line 71: | Line 72: | ||
- | 1 kWp installed PV power requires approximately 5kWh of battery: | + | 1 kWp installed PV power requires approximately 5kWh of lead acid battery: |
+ | Each additional 1 kWp of AC PV will require an additional proportional 5 kWh increase in lead acid battery storage. | ||
- | 1,5 kWp installed PV power requires: | + | 1,5 kWp installed |
+ | Each additional 1.5 kWp of AC PV will require an additional proportional 4.8 kWh increase in battery storage. | ||
===== 4 Requirement of adding DC-Coupling - MPPT Solar Chargers ===== | ===== 4 Requirement of adding DC-Coupling - MPPT Solar Chargers ===== | ||
Line 89: | Line 92: | ||
Reason: recover from deadlock situation of AC-Coupling only situation. | Reason: recover from deadlock situation of AC-Coupling only situation. | ||
+ | There is no Factor 1.0 limit that applies for DC coupled PV through a Victron MPPT. Nor is there a specific minimum amount of battery storage capacity, though please follow battery manufacture specifications for maximum charge rates. A rule of thumb is C10 (10% of Ah capacity in A) for lead acid batteries, and C2 (50% of Ah capacity in A) for lithium batteries. | ||
===== 5 Software configuration ===== | ===== 5 Software configuration ===== | ||
- | Multis and Quattros with factory settings will not shift the AC output frequency to regulate charge current. When setting up an AC Coupled system, install either the [[ess: | + | Multis and Quattros with factory settings will not shift the AC output frequency to regulate charge current. When setting up an AC Coupled system, install either the [[ess: |
+ | The Inverter RS will automatically shift frequency without any additional configuration required when a surplus/ | ||
Other options, __all deprecated__, | Other options, __all deprecated__, | ||
Line 101: | Line 108: | ||
===== Monitoring ===== | ===== Monitoring ===== | ||
- | See [[ccgx:start|section | + | See [[https:// |
ac_coupling/start.1569927115.txt.gz · Last modified: by guy_stewart
