ac_current_sensor:start
AC Current sensor
Introduction
The AC Current sensor is a simple external current sensor used to measure AC Current, Power (VA) and calculate energy of a PV inverter connected to the AC input or output of a Multi or Quattro. These values can then be displayed and sent to the VRM-website by the Color Control. The two measurement wires can be connected to the AUX and/or temperature sense input of a Multi or Quattro.
Multi and Quattro hardware requirements
  1. The Multi or Quattro needs to have the new microprocessor: make sure that the 7 digit firmware version number, as written on the microprocessor, starts with 26 or 27. Old, and therefore incompatible, control boards will have a firmware version starting with 19 or 20.
  2. The TEMP-sense input of all Multi’s and Quattro’s is suitable for the AC Current Sensor.
  3. The AUX-input however is not, see serial number list below to check your hardware.
  4. the Multi or Quattro needs to be connected on the VE.Bus port of the Color Control GX: readout will not work when connected on the VE.Can port using a VE.Bus to VE.Can interface cable.
Installation
  1. Put one of the AC wires of the PV inverter through the AC Current sensor.
  2. Connect the sensor to the AUX or TEMP-sense input of an Inverter, Multi or Quattro in the same phase as being measured by that current sensor.
  3. Configure the power range with the dipswitches. Select the power equal or higher than the maximum expected power. For example, with a 4kW PV installation, the correct dipswitch setting is 5kW.
  4. Multi-phase installations: add one AC current sensor for each phase of the PV inverter. Wire it to the Multi in the same phase.
Configuration
  1. Upgrade the Multi or Quattro firmware to the latest version (2xx). Instructions are in the VEConfigure3 requirements document. Download from: www.victronenergy.com/support-and-downloads/software
  2. Parallel and three-phase systems: configure parallel or three-phase operation first.
  3. Then use the VEConfigure3 to add and configure the 'AC Current sensor’ assistant.
  4. Parallel and three-phase systems: add the assistant to each Multi or Quattro that has an AC Current sensor connected to it.
  5. Make sure that the Color Control is running firmware version v1.11 or newer.
  6. Select the correct profile on the Color Control: Settings → System setup.
FAQ
How many AC Current Sensors can I connect in one VE.Bus system?
The current maximum is four sensors. Note that each need to be configured separately with an assistant in the Multi or Quattro to which it is wired. The maximum of four will be increased to 9, in CCGX version v1.30, planned for December 2015
Specification
Power range 1.5kW 3kW 5kW 7kW Not used
Power step size Approx depends on input voltage (230V AC) 9 17 30 35 - W
Power step size Approx depends on input voltage (120V AC) 4.5 8.5 15 17.5 - W
Max measured Current 8 16 25 30.5 - A
Max Input current 9 18 30 40 - A
Dipswitch - 1 1,2 1,2,3 1,2,3,4 ON
Protection category IP54
Supported models AUX input TEMP input
Product code Description Minimum SN# Minimum SN#
PMP123021010 MultiPlus 12/3000/120-50 - 230V HQ1352 All serial numbers
PMP123021102 MultiPlus 12/3000/120-50 120V HQ1322 All serial numbers
PMP243021010 MultiPlus 24/3000/70-50 230V HQ1350 All serial numbers
PMP243021102 MultiPlus 24/3000/70-50 120V HQ1347 All serial numbers
PMP245021010 MultiPlus 24/5000/120-100 230V HQ1326 All serial numbers
PMP485021010 MultiPlus 48/5000/70-100 230V HQ1326 All serial numbers
_
QUA123020010 Quattro 12/3000/120-50/50-230V HQ1332 All serial numbers
QUA125020000 Quattro 12/5000/220-100/100-230V HQ1347 All serial numbers
QUA125021100 Quattro 12/5000/220-100/100-120V HQ1329 All serial numbers
QUA243020010 Quattro 24/3000/70-50/50-230V HQ1341 All serial numbers
QUA245021010 Quattro 24/5000/120-100/100-230V +50A aux. HQ1326 All serial numbers
QUA248020010 Quattro 24/8000/200-100/100-230V +50A aux. HQ1333 All serial numbers
QUA483021100 Quattro 48/3000/35-50/50 120V HQ1329 All serial numbers
QUA485021010 Quattro 48/5000/70-100/100-230V +50A aux. HQ1330 All serial numbers
QUA485021100 Quattro 48/5000/70-100/100-120V/60Hz +50A aux HQ1341 All serial numbers
QUA488020000 Quattro 48/8000/110-100/100 230V. HQ1327 All serial numbers
QUA481030010 Quattro 48/10000/140-100/100 230V +50A aux HQ1326 All serial numbers
QUA488020000 Quattro 48/8000/110-100/100 230V HQ1327 All serial numbers
QUA481030010 Quattro 48/10000/140-100/100 230V +50A aux. HQ1326 All serial numbers
_
PMP243021014 Multi-G 24/3000/70-50 All serial numbers All serial numbers
PMP245021014 Multi-G 24/5000/120-100All serial numbers All serial numbers
PMP485021014 Multi-G 48/5000/70-100 All serial numbers All serial numbers
_
Other models Not yet implemented. All serial numbers
ac_current_sensor/start.1465301872.txt.gz · Last modified: by mvader