MPPT Solar Charger Error Codes
Error Codes
Err 2 - Battery voltage too high
This error will auto-reset after the battery voltage has dropped. This error can be due to other charging equipment connected to the battery or a fault in the charge controller.
Err 3, Err 4 - Remote temperature sensor failure
Check if the T-sense connector is properly connected to a remote temperature sensor. Most likely cause: the remote T-sense connector is connected to the BAT+ or BAT- terminal. This error will auto-reset after proper connection.
Err 5 - Remote temperature sensor failure (connection lost)
Check if the T-sense connector is properly connected to a remote temperature sensor. This error will not auto-reset.
Err 6, Err 7 - Remote battery voltage sense failure
Check if the V-sense connector is properly connected to the battery terminals. Most likely cause: the remote V-sense connector is connected in reverse polarity to the BAT+ or BAT- terminals.
Err 8 - Remote battery voltage sense failure (connection lost)
Err 17 - Controller overheated despite reduced output current
This error will auto-reset after charger has cooled down. Check the ambient temperature and check for obstructions near the heatsink.
Err 18 - Controller over-current
This error will auto-reset. Disconnect the charge controller from all power-sources, wait 3 minutes, and power up again. If the error persists the charge controller is probably faulty.
Err 20 - Maximum Bulk-time exceeded
This error can only occur when the maximun bulk-time protection is active. This error will not auto-reset. This error is generated when the battery-absorption-voltage is not reached after 10 hours of charging.
This protection is default disabled in all Solar Chargers.
It is default enabled on the Skylla-i and the Skylla IP44.
Our advice is to not enable it on solar chargers.
Err 21 - Current sensor issue
The charge controller is probably faulty. This error will not auto-reset.
Err 26 - Terminal overheated
Power terminals overheated, check wiring, including the wiring type and type of strands, and/or fasten bolts if possible.
Err 33 - PV over-voltage
This error will auto-reset after PV-voltage has dropped to safe limit. This error is an indication that the PV-array configuration with regard to open-circuit voltage is critical for this charger. Check configuration, and if required, re-organise panels.
Err 34 - PV over-current
The current from the solar-panel array has exceeded 75A. This error could be generated due to an internal system fault. Disconnect the charger from all power-sources, wait 3 minutes, and power-up again. If the error persists the controller is probably faulty. This error will auto-reset.
Err 38 - Input shutdown due to battery over-voltage
To protect the battery from over-charging the panel input is shut down. To recover from this condition first disconnect the solar panels and disconnect the battery. Wait for 3 minutes reconnect the battery first and next the panels. If the error persists the charge controller is probably faulty.
Information 65 - Communication warning
Communication with one of the paralleled controllers was lost. To clear the warning, switch the controller off and back on
Information 66 - Incompatible device
The controller is being paralleled to another controller that has different settings and/or a different charge algorithm.
Make sure all settings are the same and update firmware on all chargers to the latest version
Err 67 - No BMS
The charger is configured to be controlled by a BMS, but it does not receive any control messages from a BMS. The charger stopped charger, as a safety precaution.
Check the connection between the charger and the BMS.
How to reset the charger, to de-couple it from the BMS
When the charger needs to operate in stand-alone mode again, not controlled by a BMS, it needs to be reset:
- VE.Can solar chargers, go into the setup menu, and change setting ‘BMS’ from ‘Y’ to ‘N’ (setup item 31).
- VE.Direct solar chargers, reset the charger to factory defaults with VictronConnect, and then reconfigure it.
Note that (solar-)chargers automatically configure themselves to be BMS-controlled when they are connected to one.
Err 114 - CPU temperature to high
This error will reset after the CPU has cooled down. If the error persists, check the ambient temperature and check for obstructions near the air inlet and outlet holes of the charger cabinet. Check manual for mounting instructions with regard to cooling. If error persists the controller is probably faulty.
Err 116 - Calibration data lost
The unit is faulty, contact Victron.
Err 119 - Settings data lost
The charger cannot read its configuration, and stopped.
This error will not auto-reset. To get it working again:
- First, restore it to factory defaults.
- Disconnect the charge controller from all power-sources
- wait 3 minutes, and power up again.
- Reconfigure the charger.
