Introduction
This page is created to inform you on the details of NMEA 2000 PGNs that are transmitted by Victron CAN enabled products.
Switch Bank Control - PGN 127502 (0x1F20E) (deprecated)
This message is no longer transmitted and has been replaced by PGN 127501.
This applies to products with versions as specified in the table below or newer.
Product | Version |
BlueSolar MPPT 150/70 & 150/85 | v2.00 |
Lynx Shunt VE.Can | v1.00 |
Skylla-i | v2.00 |
VE.Direct to VE.Can\NMEA 2000 | v1.06 |
VE.Bus to VE.Can\NMEA 2000 | v0.12 |
Binary Status Report - PGN 127501 (0x1F20D)
This PGN is sent out by multiple products, however the details differ per product.
BlueSolar Charger 150/70 & 150/85
Signal | Meaning |
Bank Instance | Instance of the message, default value 0 |
Status 1 - Relay | “On” - The relay on the charger is active, the contact is closed |
Status 2 - Alarm | “On” - There is an alarm condition |
Status 3 - Low voltage | “On” - Battery voltage is too low |
Status 4 - High voltage | “On” - Battery voltage is too high |
Status 5 - Solar activity | “On” - Solar panel irradiated (can be used for day/night detection) |
Status 6 … 28 | Not used, reports “No Action” |
When the Alarm status bit is set to “On”, the alarm reason can be queried using Victron propietary register 0xEDDA (Charger error code).
Lynx Shunt VE.Can
Since v1.07 the Lynx Shunt also transmits PGN 127501 for the relay trigger reason next to the PGN with the alarm reason.
The mapping of the status bits is identical to the alarm message.
The default instance of the alarm message is 0, as the default instance for the relay message is 1.
Signal | Meaning |
Bank Instance | Instance of the message Default value for alarm message is 0 Default value for relay message is 1 |
Status 1 – Low voltage | “On” – Battery voltage is too low |
Status 2 – High voltage | “On” – Battery voltage is too high |
Status 3 – Low SOC | “On” – The Battery state of charge is too low |
Status 4 – Low fused voltage | “On” – Fused voltage is too low |
Status 5 – High fused voltage | “On” – Fused voltage is too high |
Status 6 – Fuse blown | “On” – The fuse is blown |
Status 7 – High battery temperature | “On” – Battery temperature is too high |
Status 8 – Low battery temperature | “On” – Battery temperature is too low |
Status 9 – High internal temperature | “On” – Internal temperature is too high |
Status 10 … 28 | Not used, report as “Unavailable” |
The alarm and relay thresholds can be configured using Victron proprietary registers.
Skylla-i
Signal | Meaning |
Status 5 … 28 | Not used, reports “No Action” |
VE.Direct to VE.Can\NMEA 2000 interface
Alarm and relay tresholds need to be configured on the BMV itself.
Signal | Meaning |
Status 3 – Low voltage* | “On” – Battery voltage is too low |
Status 4 – High voltage* | “On” – Battery voltage is too high |
Status 5 – Low SOC* | “On” – The Battery state of charge is too low |
Status 6 – Low voltage 2* | “On” – Starter Battery voltage is too low |
Status 7 – High voltage 2* | “On” – Starter Battery voltage is too high |
Status 8 … 28 | Not used, report as “No Action” |