Isolation transformer
3. Installation
3.1. What's in the box
The isolation transformer ships with the following items:
Description
1x hanging bracket, used for mounting the isolation transformer inside a vessel.
1x isolation transformer.
1x long yellow/green jumper wire with female 6.35 mm spade connectors, used to connect AC input earth (PE) to AC output earth (PE) when the vessel is out of the water for maintenance or winter storage.
1x long yellow/green wire with eye terminals, used for case grounding.
1x short yellow/green jumper wire with female 6.35 mm spade connectors, used to make AC output neutral (N) to earth (PE) link.
7x mounting screws.
3.2. Connections overview
ID
Description
1
AC input screw terminals (shore power):
Phase (Lin) neutral (Nin) and earth (PEin).
2
Male spade terminals to establish an AC output neutral to earth connection link for a correct operation of an AC output GFCI:
Connect J21 to J33 to cabinet.
3
Male spade terminals to configure the AC output voltage:
For 115V, connect J29 to J32 and connect J31 to J25.
For 230V, connect J31 to J32.
4
AC output screw terminal (AC loads or AC installation):
Phase (Lout) neutral (Nout) and earth (PEout).
5
Male spade terminals to bridge AC input earth to AC output earth when the vessel is out of the water:
Connect PEin (J34A and/or J34A1) to J34.
3.3. AC output configuration
The AC output needs to be configured for 115 or 230V use. This is done by connecting male spade terminals using the black jumper wires (included). These terminals are located above the AC output connector.
AC output voltage
Connect jumper cable between
Connections
115V
J29 and J32
J31 and J25
230V
J31 and J32
3.4. Connecting AC input and AC output
Warning
Shock hazard. Do not work on the isolation transformer or the electrical system if still connected to an electrical power source.
Connection sequence:
  1. Pass the AC cables through the cable glands at the bottom of the cabinet in the following way:
    1. Pass the AC input (shore power) cable through the left side cable gland.
    2. Pass the AC output (AC loads) cable through the right side cable gland.
  2. Connect the AC input cable to the INPUT terminal block in the following way:
    1. Connect the earth wire to the PE terminal.
    2. Connect the neutral wire to the N terminal.
    3. Connect the phase wire to the L terminal.
  3. Connect the AC output cable to the OUTPUT terminal block in the following way:
  4. Connect the enclosure to the ground (=all the metal parts in the vessel) in the following way:
    1. Connect the M6 bolt underneath the enclosure to the vessel ground. See the below drawing for the location of the chassis earth bolt.
Location of the chassis earth bolt.
3.5. AC output neutral to earth link
A GFCI must be installed in the AC output of the isolation transformer. For the GFCI to operate correctly, the AC output neutral must be connected to the AC output earth and ground (= all the metal parts in the vessel).
To link the AC output neutral (N) to earth (PE), place a green/yellow jumper wire (included) between the J33 and J21 male spade connectors.
3.6. Cable cross-section requirements
Use the following minimal cable cross-sections:
Isolation transformer power rating
Voltage
Metric
AWG
3600W
115V
6mm²
AWG 10
3600W
230V
2.5mm²
AWG 13
3.7. Wiring example
Wiring example isolation transformer installed on a vessel connected to shore power.
ID
Description
A
Shore power.
B
Circuit breaker.
C
GFCI (Ground Fault Circuit Interrupter).
D
Shore cable.
Isolation transformer.
F
AC loads.
3.8. Linking input and output earth when the vessel is out of the water.
For safety reasons, when the vessel is out of the water (on land) during winter or for maintenance, the vessel's earth (PE) conductor must be connected directly to the shore power earth (PE) conductor.
This can be achieved inside the isolation transformer by connecting the yellow/green jumper wire (included) between male spade terminals J34A and J34, as indicated below.
AC input earth is connected to AC output earth when the vessel is out of the water (on land) during winter or for maintenance.
