Quattro-II 2x120V
5. Configuration
This section is intended mainly for stand-alone applications.
Warning
Settings may only be changed by a qualified electrical engineer.
Read the instructions thoroughly before implementing changes.
During the configuration of the charger, the AC input must be removed.
5.1. Standard settings: ready for use
On delivery, the inverter/charger is set to standard factory values. These settings are generally suitable for single-unit operation.
Warning
It is a possibility that the standard charging voltage does not suit your batteries. Consult the manufacturer's documentation or your battery supplier.
Setting
Default value
Inverter frequency
60Hz
Input frequency range
45 - 65Hz
Input voltage range
Split phase 180 - 280VAC; Single phase: 90 - 140VAC
Inverter voltage
120VAC
Stand-alone, parallel or 3-phase
stand-alone
AES (Automatic Economy Switch)
off
Ground relay
on
Charger on/ off
on
Battery charge curve
four-stage adaptive with BatterySafe mode
Charging current
100% of the maximum charging current
Battery type
Victron Gel Deep Discharge (also suitable for Victron AGM Deep Discharge)
Automatic equalisation charging
off
Absorption voltage
14.4V / 28.8V
Absorption time
up to 8 hours (depending on bulk time)
Float voltage
13.8V / 27.6V
Storage voltage
13.2V / 26.4V (not adjustable)
Repeated absorption time
1 hour
Absorption repeat interval
7 days
Bulk protection
on
AC input current limit
50A for both AC inputs
UPS feature
on
Dynamic current limiter
off
WeakAC
off
BoostFactor
2
Programmable relay
alarm function
PowerAssist
on
5.2. Explanation of settings
Settings that are not self-explanatory are described briefly below. For further information, please refer to the help files in the software configuration programs. See the Configuring chapter.
Inverter frequency
Output frequency if no AC is present at the input.
Adjustability: 50 Hz; 60 Hz
Input frequency range accepted by the Quattro-II. The Quattro-II synchronises within this range with the AC input frequency. The output frequency is then equal to the input frequency.
Adjustability: 50, 60 or 45 – 65 Hz.
Input voltage range
Voltage range accepted by the Quattro-II. The Quattro-II synchronises within this range with the AC input. The output voltage is then equal to the input voltage.
Adjustability:
Lower limit: 90 – 120V / 180 – 240V
Upper limit: 120 – 140V / 240 – 280V
Note
The standard lower limit setting of 90V is intended for connection to a weak mains supply, or to a generator with unstable AC output. This setting may result in a system shut down when connected to a ‘brushless, self-excited, externally voltage regulated, synchronous AC generator’ (synchronous AVR generator). Most generators rated at 10kVA or more are synchronous AVR generators. The shutdown is initiated when the generator is stopped and revs down while the AVR simultaneously ‘tries’ to keep the output voltage of the generator at 120V.
The solution is to increase the lower limit setting to 110VAC (the output of AVR generators is generally very stable), or to disconnect the inverter/charger from the generator when a generator stop signal is given (with the help of an AC contactor installed in series with the generator).
Inverter voltage
Output voltage of the Quattro-II in battery operation.
Adjustability: 95 - 128V
Stand-alone / parallel operation / 2-phase / 3-phase setting
Using several devices, it is possible to:
  • Increase the total inverter power by connecting several devices in parallel.
  • Create a split-phase system with a separate autotransformer: see the Victron Autotransformer product page.
  • Create a 3-phase system.
The standard product settings are for standalone operation. For parallel, three-phase or split-phase operation, see the Configuring chapter.
If this setting is turned ‘on’, the power consumption in no-load operation and with low loads is decreased by approximately 20%, by slightly 'narrowing' the sinusoidal voltage. Applicable in stand-alone configuration only.
Search Mode
Instead of the AES mode, the search mode can also be chosen. If search mode is ‘on’, the power consumption in no-load operation is decreased by approximately 70%. In this mode the Quattro-II, when operating in inverter mode, is switched off in case of no load or very low load, and switches on every two seconds for a short period. If the output current exceeds a set level, the inverter will continue to operate. If not, the inverter will shut down again.
The Search Mode ‘shut down’ and ‘remain on’ load levels can be set with VEConfigure.
The standard settings are:
Shut down: 48 Watt (linear load)
Turn on: 72 Watt (linear load)
Ground relay (see appendix B)
With this relay, the neutral conductor of the AC output is grounded to the chassis when the AC input relays are open. This ensures the correct operation of earth leakage circuit breakers in the AC output.
Battery charge algorithm
The standard setting is ‘Four-stage adaptive with BatterySafe mode’. See Section 2 for a description.
This is the recommended charge algorithm for lead acid batteries. See the help files in the software configuration programs for other features.
Battery type
The standard setting is the most suitable for Victron Gel Deep Discharge, Gel Exide A200, and tubular plate stationary batteries (OPzS).
This setting can also be used for many other batteries: e.g. Victron AGM Deep Discharge and other AGM batteries, and many types of flat-plate flooded batteries.
With VEConfigure the charge algorithm can be adjusted to charge any battery type (Nickel Cadmium batteries, Lithium-ion batteries).
Absorption time
In case of the standard-setting ‘Four-stage adaptive with BatterySafe mode’ the absortion time depends on the bulk time (adaptive charge curve), so that the battery is optimally charged.
This setting is intended for flooded tubular plate traction or OPzS batteries. During the absorption stage, the voltage limit increases to 2.83V/cell (34V for a 24V battery and 68V for a 48V battery) once the charge current has dropped to less than 10% of the set maximum current.
Not adjustable with DIP switches.
See ’tubular plate traction battery charge curve’ in VEConfigure.
Storage voltage, Repeated Absorption Time, Absorption Repeat Interval
See Section 2.
Bulk Protection
When this setting is ‘on’, the bulk charging time is limited to 10 hours. A longer charging time could indicate a system error (e.g. a battery cell short-circuit).
These are the current limit settings for which PowerControl and PowerAssist come into operation:
Inverter rating
PowerAssist setting range, grid in-line topology
PowerAssist setting range, grid parallel topology with external 50 or 100A current transformer
3000VA
9.5 - 50A
9.5 - 50/100A
5000VA
11 - 100A
11 - 100A
Factory setting: 30A
UPS feature
If this setting is ‘on’ and AC on the input fails, the Quattro-II switches to inverter operation practically without interruption.
The output voltage of some small generator sets is too unstable and distorted for using this setting – the Quattro-II would continually switch to inverter operation. For this reason, the setting can be turned off. The Quattro-II will then respond less quickly to AC input voltage deviations. The switchover time to inverter operation is consequently slightly longer, but most equipment (most computers, clocks or household equipment) is not adversely impacted.
Recommendation: Turn the UPS feature off if the Quattro-II fails to synchronise, or continually switches back to inverter operation.
Intended for generators, the AC voltage being generated by means of a static inverter (so-called ‘inverter’ generators). In these generators, engine rpm is reduced in case of low load: this reduces noise, fuel consumption and pollution. A disadvantage is that the output voltage will drop severely or even completely fail in the event of a sudden load increase. More load can only be supplied after the engine is up to speed.
If this setting is ‘on’, the Quattro-II will start supplying extra power at a low generator output level and gradually allow the generator to supply more, until the set current limit is reached. This allows the generator engine to get up to speed.
This setting is also often used for ‘classical’ generators that respond slowly to sudden load variation.
Weak AC
Strong distortion of the input voltage can result in the charger hardly operating or not operating at all. If WeakAC is set, the charger will also accept a strongly distorted voltage, at the cost of greater distortion of the input current.
Recommendation: Turn WeakAC on if the charger is hardly charging or not charging at all (which is quite rare!). Also turn on the dynamic current limiter simultaneously, and reduce the maximum charging current to prevent overloading the generator if necessary.
Note
When WeakAC is on, the maximum charge current is reduced by approximately 20%.
BoostFactor
Change this setting only after consulting with Victron Energy or with an engineer trained by Victron Energy!
Programmable relay
The relay can be programmed for all kinds of other applications, for example as a starter relay for a generator.
Auxiliary AC output (AC-out-2)
Intended for non-critical loads and directly connected to the AC input. With current measurement circuit to enable PowerAssist.
5.3. Configuring
The following hardware is required:
5.3.1. VictronConnect app
The MultiPlus is configured using the VictronConnect app.
More general information about the VictonConnect app, like how to install it, how to pair it with your device, and how to update firmware, can be found by referring to the overall VictronConnect manual.
5.3.2. VEConfigure
All settings can be changed with a PC and free of charge software VEConfigure, downloadable from our website www.victronenergy.com.
See the VEConfigure manual for more information.
5.3.3. VE.Bus Quick Configure Setup
VE.Bus Quick Configure Setup is a software program with which systems with a maximum of three inverters/chargers can be configured in parallel or three-phase in a simple manner.
The software can be downloaded free of charge at www.victronenergy.com.
5.3.4. VE.Bus System Configurator
For configuring advanced applications and/or systems with four or more Multis, VE.Bus System Configurator software must be used.