Quattro-II | 12/3000/120-50 2x120V | 24/3000/70-50 2x120V | ||
PowerControl & PowerAssist | Yes (on L1 input) | |||
Transfer switch | 50A | |||
Maximum AC input current | 50A (each leg) | |||
INVERTER | ||||
DC Input voltage range | 9.5 – 17V | 19 - 33V | ||
Output in inverter mode (1) | Output voltage: 120VAC ± 2% Frequency: 60Hz ± 0.1% | |||
Cont. output power at 25°C (3) | 3000VA | |||
Cont. output power at 25°C | 2400W | |||
Cont. output power at 40°C | 2200W | |||
Cont. output power at 65°C | 1700W | |||
Maximum apparent feed-in power | 2500VA | |||
Peak power | 5500W | |||
Maximum efficiency | 93% | 94% | ||
Zero load power | 15W | 11W | ||
Zero load power in AES mode | 10W | 8W | ||
Zero load power in Search mode | 4W | 4W | ||
Maximum output current | 60A peak, 50Arms for 1seconds | |||
CHARGER | ||||
AC Input | Split phase: 180-280VAC 45 – 65Hz Single phase: 90-140VAC 45 – 65Hz | |||
Charge voltage 'absorption' | 14.4V | 28.8V | ||
Charge voltage 'float' | 13.8V | 27.6V | ||
Storage mode | 13.2V | 26.4V | ||
Maximum battery charge current (4) | 120A | 70A | ||
Battery temperature sensor | Yes | |||
GENERAL | ||||
Auxiliary output (5) | Yes (50A) | |||
Programmable relay (6) | Yes | |||
Protection (2) | a – g | |||
VE.Bus communication port | For parallel and three-phase operation, remote monitoring and system integration | |||
General purpose communication port (7) | Yes, 2x | |||
Remote on-off | Yes | |||
Operating temperature range | -40 to +65°C (-40 - 150°F) fan assisted cooling | |||
Humidity (non-condensing) | max 95% | |||
ENCLOSURE | ||||
Material & Colour | Steel, blue RAL 5012 | |||
Protection category | IP22 | |||
Battery-connection | 2x2 M8 bolts | 2 M8 bolts | ||
120/240VAC-connection | Screw terminals 21mm² (4 AWG) | |||
Weight | 23.8 kg ( 52 lb) | 22.5 kg (50 lb) | ||
Dimensions hxwxd | 579 x 319 x 168 mm 23 x 13 x 7 inch | |||
STANDARDS | ||||
Safety | EN-IEC 60335-1, EN-IEC 60335-2-29 | |||
Emission, Immunity | EN 55014-1, EN 55014-2 EN-IEC 61000-3-2, EN-IEC 61000-3-3 IEC 61000-6-1, IEC 61000-6-2, IEC 61000-6-3 | |||