Includes:
Internally pre-wired enclosure.
A built-in AC bypass switch with full system current capability, and a DC disconnect breaker for safe and easy isolation for servicing of the inverter and/or battery bank.
Battery to inverter/charger DC disconnect breaker (250 Amps).
Inverter AC input overcurrent protection breakers.
DIN mount AC and DC breakers for quick and easy operation.
A500A/50mV DC shunt installed for easy connection to battery status monitor.
Enclosure and components are UL/CSA certified and designated for indoor use.
Configurations available for both single 120 and 230 VAC, 120/240 VAC and 3-Phase systems.
DC negative, positive and ground busbars for DC loads and PV arrays included.
Mounting provided for DIN rail DC load/disconnect breakers.
Integrates directly with Victron Energy’s 3,000 and 5,000 MultiPlus and Quattro inverter/chargers.
Knockouts for inverter/charger and battery cables, PV in/out, DC panel mount breakers.
The VE Panel (VEP) is designed for the 3kVA and 5kVA MultiPlus and Quattro inverter/chargers.
Description | Part Number |
VE.Panel 3kVA 120/240 NA Primary 24/48Vdc | VEP230121402 |
VE.Panel 3kVA 120 NA Follower 24/48Vdc | VEP230141204 |
VE.Panel MultiPlus-II 3kVA 120 Primary 48Vdc with bypass | VEP230185208 |
VE.Panel MultiPlus-II 3kVA 120 Follower 48Vdc without bypass | VEP230205210 |
VE.Panel 5kVA 120/240 NA Primary 48Vdc | VEP250125402 |
VE.Panel 5kVA 120 NA Follower 48Vdc | VEP250145204 |
VE.Panel 5kVA NA 3PH Primary 48Vdc | VEP250165606 |
Use this installation manual to aid in installation.
The installation of an electrical system such as this, fall under the guidelines of the NEC in the USA. Canadian electrical codes have jurisdiction in Canada.
These instructions are not intended to be used in lieu of these local and federal codes, but rather are used as specific to this product.
You may need to consult with a professional solar installer or electrical inspector when in doubt on code specific questions and system installation issues.
Even though the VE Panel incorporates and simplifies numerous separate electrical circuits into one enclosure, an inverter system such as this is still a very sophisticated and somewhat complicated electrical system.
![]() | WARNING: Incorrect installation or servicing may result in a risk of electric shock, fire, or other safety hazard. |