Lithium NG 51,2V battery manual
8. Technical data
8.1. Battery specification
VOLTAGE AND CAPACITY
Battery model
LFP 51,2 V/100 Ah
Nominal voltage
51,2 V
Nominal capacity @ 25 °C*
100 Ah
Nominal energy @ 25 °C*
5120 Wh
Capacity loss
(per 100 cycles, @ 25 °C, 100 % DoD): <1 %
Energy loss
Round trip efficiency
92 %
* Discharge current ≤ 1C
CYCLE LIFE (capacity ≥ 80% of nominal)
80 % DoD
2500 cycles
70 % DoD
3000 cycles
50 % DoD
5000 cycles
DISCHARGE
Max continuous discharge current (C-rate)
100 A (1C)
Max pulse discharge current 10s (C-rate)
200 A (2C)
End of discharge voltage
44,8 V
Internal resistance
8 mΩ
CHARGE
Charge voltage
Between 56 V and 56,8 V
Float voltage
54 V
Max continuous charge current (C-rate)
100 A (1C)
Max pulse charge current 10s (C-rate)
200 A (2C)
GENERAL
BMS-es
Lynx Smart BMS NG 500 A / 1000 A (M10 busbars), must be purchased separately
Cell measurements
Cell voltages and temperatures, battery current
Battery BMS interface
Male + female cable with M8 circular connector with high-speed digital communication, length 50 cm
M8 extension cables are available separately for purchase in various lengths between 1 and 5 meters
Alarm feature
Pre-alarm contact on BMS
Bluetooth
In the BMS
Max batteries per BMS
25 (128 kWh per BMS 3))
Battery firmware updates
Battery firmware automatically updated by BMS
Repairable
Yes (cover can be removed with screws)
OPERATING CONDITIONS
Operating temperature
Discharge: -20 °C to +50 °C | Charge: +5 °C to +50 °C
Storage temperature
-45 °C to +70 °C
Humidity (non-condensing)
Max. 95 %
Protection class
IP65
MOUNTING
Mounting options
Strap or mounting brackets (brackest included)
Can be placed on their sides
Yes 2)
OTHER
Self-discharge rate
≤ 3 % per month @ 25 °C
Power connection
M8 (threaded inserts and bolts)
Dimensions (h x w x d) (mm)
235 x 648 x 162
Weight (est.)
37 kg
STANDARDS
Safety
Cells: UL1973 UL9540A IEC62619 (all three pending)
Battery:  IEC62619 (pending)
EMC
EN 61000-6-3, EN 61000-6-2
Automotive
ECE R10-6 (pending)
Performance
IEC 62620 (pending)
1) When fully charged
2) The lithium battery can be mounted upright and on its side, but not with the battery terminals facing down
3) Up to 5 BMS-es can be paralleled.
8.2. Enclosure dimensions
LiFePO4_Battery_25_6V200Ah_51_2V100Ah_NG__BAT524120620_BAT548110620_.pdf