MPPT 75/10 | MPPT 75/15 | MPPT 100/15 | MPPT 100/20 | |
Battery voltage (auto select) | 12V or 24V | 12V, 24V, or 48V | ||
Maximum battery current | 10A | 15A | 15A | 20A |
Nominal PV power, 12V 1a,b | 145W | 220W | 220 W | 290W |
Nominal PV power, 24V 1a,b | 290W | 440W | 440 W | 580W |
Nominal PV power, 48V 1a,b | - | - | - | 1160W |
Max. PV short circuit current 2 | 10A | 15A | 15A | 20A |
Automatic load disconnect | Yes | |||
Maximum PV open circuit voltage | 75V | 100V | ||
Peak efficiency | 98% | |||
Self consumption | 12V: 20mA / 24V: 10mA | 12V: 25mA 24V / 48V: 15mA | ||
Charge voltage 'absorption' | 14.4V / 28.8V / 57.6V (adjustable) | |||
Charge voltage 'float' | 13.8V / 27.6V / 55.2V (adjustable) | |||
Charge voltage 'equalization' 3 | 16.2V / 32.4V / 64.8V (adjustable) | |||
Charge algorithm | Multi-stage adaptive or user defined algorithm | |||
Temperature compensation | 12V: -16mV/°C / 24V: -32mV/°C / 48V: -64 mV/°C | |||
Continuous load current | 15A | 12V & 24V: 20A 48V: 1A | ||
Low voltage load disconnect | 11.1V / 22.2V / 44.4V or 11.8V / 23.6V / 47.2V or BatteryLife algorithm | |||
Low voltage load reconnect | 13.1V / 26.2V / 52.4V or 14V / 28V / 56V or BatteryLife algorithm | |||
Protection | PV reverse polarity, output short circuit, over temperature | |||
Operating temperature | -30°C to +60°C (full rated output up to 40°C) | |||
Humidity | 100%, non-condensing | |||
Maximum altitude | 5000m (full rated output up to 2000m) | |||
Environmental condition | Indoor type 1, unconditioned | |||
Pollution degree | PD3 | |||
Data communication | VE.Direct port 4 | |||
ENCLOSURE | ||||
Colour | Blue (RAL 5012) | |||
Power terminals | 6mm² / AWG10 | |||
Protection category | IP43 (electronic components), IP22 (connection area) | |||
Weight | 0.5kg | 0.6kg | 0.65kg | |
Dimensions (h x w x d) | 100 x 113 x 40mm | 100 x 113 x 50mm | 100 x 131 x 60mm | |
STANDARDS | ||||
Safety | EN/IEC 62109-1 / UL 1741 / CSA C22.2 NO.107.1-16 | |||
1a) The solar charger will limit input power if more PV power is connected. 1b) The PV voltage must exceed Vbat + 5V for the controller to start. Thereafter the minimum PV voltage is Vbat + 1V. 2) A higher short circuit current may damage the solar charger in case of reverse polarity connection of the PV array. 3) Equalization is by default disabled. 4) For more information on data communication see the data communication paper in the Technical information section on our website. |