8. Technical data
8.1. Technical specifications
VM-3P75CT | REL200300100 |
VOLTAGE INPUTS | |
Voltage connection | Direct |
Input voltage range L-N | 85 to 265VAC |
Input voltage range L-L | 150 to 460VAC |
Frequency | 50/60Hz |
CURRENT INPUTS | |
Current connection | Via current transformers (included - wire length 640mm (25.2in) |
Rated current | 75A |
COMMUNICATION | |
VE.Can communication port | Two RJ45 connectors (VE.Can terminators included) |
Ethernet communication port | One RJ45 connector, Modbus UDP |
Refresh rate | 100ms |
POWER SUPPLY | |
Type | Self-power supply via L1-N |
Switch or circuit breaker | Required as means of a disconnecting device - not included |
External fuse [1] | Required in the neutral conductor - 500mA, not included |
Consumption | 1.45W / 3.1VA |
ENCLOSURE | |
Material & colour | Polycarbonate, blue (RAL5012) |
Voltage connection | Screw terminals 0.25 - 1.5mm2 (24 - 16AWG) |
Current transformer connection | Pluggable screw terminals (included) |
Protection category | IP20 |
Weight | 370g (including packaging) |
Dimensions | 90 x 71 x 59mm (3.5 x 2.8 x 2.3in) |
ENVIRONMENTAL | |
Indoor/outdoor usage | Indoor only |
Operating temperature | From -10 to +55 °C |
Storage temperature | From -20 to +70 °C |
Relative humidity | < 90% non-condensing |
Altitude | 2000m (6562ft) |
Mains supply voltage fluctuations | ±0.1Vin |
Overvoltage category | Cat. III |
Pollution degree | 2 |
STANDARDS | |
Safety | EN-IEC 61010-1 |
[1] Can be omitted if a circuit breaker with a fuse rating of 500mA is used as the isolating device. |
8.2. Enclosure dimensions
![DimensionDrawing_Energy_Meter_VM-3P75CT-rev00.pdf](image/166795656803db.png)