The Lynx Smart BMS NG will power up when a battery is connected, the wire loop is placed between pins 10 and 11 of the multi-connector, or the Remote on/off switch is switched on.
When first powered on and after a “Reset to defaults” (via the VictronConnect app), the Lynx Smart BMS NG automatically determines and sets the following settings:
System voltage, 12, 24 or 48V, by measuring the battery voltage
Number of batteries in parallel, series and parallel/series configuration
Number of battery cells per battery
A firmware update of the Lynx Smart BMS NG can be performed in two different ways:
Via the VictronConnect app
Via the VRM: Remote Firmware Update feature (requires an internet-connected GX device)
Notes on firmware updating in general
Newer is not always better
Don't break it if it works
Be sure to read the changelog before starting the update process. The changelog can be downloaded from Victron Professional.
Therefore, use this feature with care. Our main advice is not to update a running system unless there are problems with it or before the first startup.
Notes on updating the Lynx Smart BMS NG firmware
A firmware update will not result in a temporary system shutdown. During the update, the Lynx Smart BMS NG keeps all contacts and the contactor in the same state as when starting the update. If the update fails, ATD/ATC and contactor open after 120 seconds for safety reasons. This also gives time to try updating again.
Updating the firmware always starts a new full charging cycle despite the SoC threshold setting, which means that the charge voltage limit (CVL) is automatically adjusted from 13.5V to 14.0V (28.0V or 56.0V).
Updating firmware via VictronConnect
Please note the following before performing a firmware update via VictronConnect:
For detailed instructions on updating the firmware, see the firmware update chapter in the VictronConnect manual.
If a newer firmware version is available, the VictronConnect app (make sure the VictronConnect app is the latest version) will notify you as soon as a connection with the Lynx Smart BMS NG is made.
Updating firmware via VRM: Remote firmware update
Features:
Remotely update internet-connected products straight from the VRM Portal
No need to install any software
Works from laptop, tablet & phone
There is no need to find the right firmware file: the system has all of them and will clearly indicate that a newer version is available.
See the VRM: Remote firmware update manual for detailed instructions.
Once powered up, use the VictronConnect app to configure the BMS settings.
Check the Battery voltage setting (12, 24 or 48V):
Check the Battery capacity setting:
Check the Number of batteries in parallel:
Check the Pre-alarm mode setting: This setting is automatically configured upon initial power-up and after a "Reset to defaults". It is enabled by default.
Set the Relay mode: The programmable relay has two operation modes: Alarm relay and Alternator ATC.
DVCC settings: DVCC is forced on and cannot be turned off. However, a few settings can be changed, which are described below. Please note that these settings only affect compatible DVCC devices such as Victron inverter/chargers, Orion XS DC-DC battery chargers and Solar MPPT chargers.
Battery monitor settings: Unlike other battery monitors, the Lynx Smart BMS NG battery monitor settings are mostly fixed and not customisable. This is because the Lynx Smart BMS NG is always used together with Victron Lithium NG batteries, and many battery monitor parameters are known because they relate to the battery type. The following settings are adjustable. A full list of all settings used can be found in List of battery monitor settings in the appendix.
These instructions only apply if the system contains one or more Lynx Distributors.
Each Lynx distributor must be addressed and set to A, B, C or D. This is done via a 2-way dip switch located inside the Lynx Distributor. Refer to chapter 6.1.3. Addressing Lynx Distributor in the Lynx distributor manual.
Tip
If the dip switches have been accidentally programmed incorrectly or need to be reprogrammed to a different address after commissioning the Lynx Smart BMS NG, you must restart the BMS (OFF mode and back to Standby or ON mode). This action is necessary to correctly adopt the Lynx Distributor status in VictronConnect and the GX device. Restarting the BMS will also reset the error message "W-D02: Communication with Distributor [A, B, C, or D] lost" in VictronConnect and clear the Lynx Smart BMS alarm "Distributor [A, B, C, or D] connection lost."
Use the VictronConnect app to give each fuse a custom name (maximum 16 characters). If the fuse name is empty (0 characters), the fuse will be disabled and ignored for monitoring.