VE.Bus BMS V2
5. Operation
5.1. Important warning
Lithium batteries are expensive and can be damaged due to over discharge or over charge. Damage due to over discharge can occur if small loads (such as: alarm systems, relays, standby current of certain loads, back current drain of battery chargers or charge regulators) slowly discharge the battery when the system is not in use. In case of any doubt about possible residual current draw, isolate the battery by opening the battery switch, pulling the battery fuse(s) or disconnecting the battery plus when the system is not in use.
A residual discharge current is especially dangerous if the system has been discharged completely and a low cell voltage shutdown has occurred. After shutdown due to low cell voltage, a capacity reserve of approximately 1Ah per 100Ah battery capacity is left in the battery. The battery will be damaged if the remaining capacity reserve is drawn from the battery. A residual current of 10mA for example may damage a 200Ah battery if the system is left in discharged state for more than 8 days.
The shutdown due to low cell voltage by the BMS should always be used as a last resort to be on the safe side at all times. We recommend not letting it get that far in the first place and instead shutting down the system automatically based on a defined state of charge so that there is enough reserve capacity in the battery. For an inverter/charger, for example, this can be done via the VE.Configure setting 'shut-down on SoC'. It is even easier with a BMV, whose relay can control the remote on/off port of the BMS via an adjustable SoC value.
5.2. LED indications
LED
Colour
Behaviour
Meaning
Status
Blue
Off
BMS is off
Lights shortly approximately once every 10 seconds.
BMS is operating normally.
Flashes rapidly at approximately 15 times per second.
The BMS is stuck in boot loader mode due to a faulty application.
Cell > 2.8V
Blue
Off
Low cell voltage.
The BMS has switched the DC loads and the inverter off.
Charge the battery or connect an AC supply to the inverter/charger. Once the battery voltage has increased sufficiently, the DC loads and inverter will be switched on again.
On
Cell voltage within normal range.
Cell > 4V
Red
Off
Cell voltage and temperature within normal range.
On
High cell voltage or high temperature.
The BMS has switched off the chargers.
Check for a faulty charger and/or reduce battery temperature. Once the battery voltage and/or temperature have been sufficiently reduced, the BMS will switch the chargers back on.