For unexpected behaviour or suspected product faults, refer to this chapter.
Start by checking the common issues described here. If the problem persists, contact the point of purchase (Victron dealer or distributor) for technical support.
If you're unsure who to contact or if the point of purchase is unknown, refer to the Victron Energy Support webpage.
This error will auto-reset after the battery voltage has dropped. This error can be due to other charging equipment connected to the battery or a fault in the charge controller.
Check if the T-sense connector is properly connected to a remote temperature sensor. Most likely cause: the remote T-sense connector is connected to the BAT+ or BAT- terminal. This error will auto-reset after proper connection.
Check if the T-sense connector is properly connected to a remote temperature sensor. This error will not auto-reset.
Check if the V-sense connector is properly connected to the battery terminals. Most likely cause: the remote V-sense connector is connected in reverse polarity to the BAT+ or BAT- terminals.
High DC ripple is usually caused by loose DC cable connections and/or too thin DC wiring. After the inverter has switched off due to high DC ripple voltage, it waits 30 seconds and then restarts.
After three restarts followed by a shutdown due to high DC ripple within 30 seconds of restarting, the inverter will shutdown and stops retrying. To restart the inverter, switch it Off and then On.
Continuous high DC ripple reduces the inverter life expectancy
The charger is stopped to avoid charging LiFePO4 batteries at low temperature as this damages the cells.
Solar Chargers
The maximum bulk time protection is a feature that was in the chargers when they were just released (2015 or earlier) and later the feature was removed.
If you do see this error, then update to the latest firmware.
If you then still have the error, perform a reset to factory defaults of the configuration, and reconfigure the solar charger.
AC Chargers
This protection is default enabled on the Skylla-i and the Skylla IP44.
This error is generated when the battery-absorption-voltage is not reached after 10 hours of charging.
The feature of this safety protection is to detect a shorted cell; and stop charging.
The internal temperature measurements are out of range. Disconnect all wires, and then reconnect all wires, to restart the unit. This error will not auto-reset. If the error remains, please contact your dealer, there might be a hardware defect.
Power terminals overheated, check wiring, including the wiring type and type of strands, and/or fasten bolts if possible.
This error will auto-reset.
This error will auto-reset. If the error does not auto-reset disconnect the charge controller from all power-sources, wait 3 minutes, and power up again. If the error persists the charge controller is probably faulty.
Disconnect all wires, and then reconnect all wires. If the error persists the charge controller is probably faulty.
Note that this error was introduced in v1.36. So when doing an update, it might look like the firmware update caused this issue; but it doesn't. The Solar charger was then already not performing 100% before the update; updating to v1.36 or later merely made the issue more visible. The unit needs to be replaced.
This error will auto-reset. This protection looks at the actual battery voltage and compares this to the settings. In case your actual voltage is above what is expected it shuts down to isolate the battery from the rest of the unit. Firstly check battery settings (absorption/float voltages) to see if something is wrong here. Another possible cause is an over-sized PV array configuration, if there are too many panels in series the battery voltage cannot be reduced any further. Consider modifying PV panel wiring to reduce the PV voltage.
The voltage difference between Neutral and Ground is too high.
Inverter or Multi (not connected to the grid):
The internal ground relay is activated but the voltage over the relay is too high. The relay might be damaged.
Multi (connected to the grid):
The ground wire in the installation is not present or not connected properly.
Line and Neutral are swapped in the installation.
This error will not auto-reset. Check the installation and restart the unit using the power-switch.
Some loads like motors or pumps draw large inrush currents in a start-up situation. In such circumstances, it is possible that the start-up current exceeds the over current trip level of the inverter. In this case the output voltage will quickly decrease to limit the output current of the inverter. If the over current trip level is continuously exceeded, the inverter will shut down: wait 30 seconds and then restart.
The Inverter can supply more power than the nominal power level for a short time. If the time is exceed the inverter stops.
After three restarts followed by another overload within 30 seconds of restarting, the inverter will shutdown and remain off. To restart the inverter, switch it Off, then On.
If the error persists reduce the load on the AC out terminal by switching off or disconnecting appliances.
A high ambient temperature or enduring high load may result in shut down to over temperature. Reduce load and/or move inverter to better ventilated area and check for obstructions near the fan outlets.
The inverter will restart after 30 seconds. The inverter will not stay off after multiple retries.
If the battery voltage is getting low and a large load is applied to the AC output the inverter is unable to maintain the proper output voltage. Re-charge the battery or reduce the AC loads to continue operation.
The inverter performs diagnostic tests before it activates its output. In the case that one of these tests fails an error message is displayed and the inverter does not turn on.
First try to restart the inverter, by switching it Off, and then On. If error persists the inverter is probably faulty.
There is already AC voltage on the AC out terminal before switching on the inverter. Check that the AC out is not connected to a mains outlet or to another inverter.
Communication with one of the paralleled controllers was lost. To clear the warning, switch the controller off and back on
The controller is being paralleled to another controller that has different settings and/or a different charge algorithm.
Make sure all settings are the same and update firmware on all chargers to the latest version
The charger is configured to be controlled by a BMS, but it does not receive any control messages from a BMS. The charger stopped charging, as a safety precaution.
This Error only shows when there is solar power available and thus the Solarcharger is ready to initiate charging. It does not show at night. And in case there is a permanent problem, the error will raise in the morning and clear at night, and so forth.
Check the connection between the charger and the BMS.
How to reconfigure the charger to standalone mode
Our Chargers and Solarchargers automatically configure themselves to be BMS-controlled when they are connected to one; either direct or via a GX Device. And that setting is semi-permanent: power cycling the charger will not reset it.
Here is what needs to be done to make the charger operate in stand-alone mode again, ie. not controlled by a BMS:
VE.Can solar chargers, go into the setup menu, and change setting ‘BMS’ from ‘Y’ to ‘N’ (setup item 31).
VE.Direct solar chargers, reset the charger to factory defaults with VictronConnect, and then reconfigure it.
Applies to SmartSolar/BlueSolar MPPTs VE.Can (FW version v1.04 or higher) and SmartSolar VE.Direct MPPTs (FW version v1.47).
To clear the error on the SmartSolar VE.Direct MPPTs update the FW version to v1.48 or higher.
To clear the error on the SmartSolar/BlueSolar MPPTs VE.Can, update the software. If the error persists, it will be because the charger is connected with both a VE.Direct cable and on VE.Can. That is not supported. Remove one of the two cables. The error will disappear and the charger will resume normal operation, within a minute.
This error will reset after the CPU has cooled down. If the error persists, check the ambient temperature and check for obstructions near the air inlet and outlet holes of the charger cabinet. Check manual for mounting instructions with regard to cooling. If error persists the controller is probably faulty.
If the unit does not work and error 116 pops up as the active error the unit is faulty, contact your dealer for a replacement.
If the error is only present in the history data and the unit operates normally this error can be ignored safely. Explanation: when the units power up for the very first time in the factory, it does not have calibration data and an error 116 is logged. Obviously this should have been cleared, but in the beginning units left the factory with this message still in the history data.
SmartSolar models (not the BlueSolar models): upgrading to v1.4x firmware is a one-way trip, you cannot go back to an older firmware version once you upgrade to v1.4x. Reverting to older firmware gives error 116 (calibration data lost), this can be fixed by re-installing the v1.4x firmware.
The charger cannot read its configuration, and stopped.
This error will not auto-reset. To get it working again:
First, restore it to factory defaults. (top right in Victron Connect, click on the three dots)
Disconnect the charge controller from all power-sources
Reconfigure the charger.
Please report this to your Victron dealer and ask them to escalate the matter to Victron; as this error should never happen. Preferably include firmware version and any other specifics (VRM URL, VictronConnect screenshots or similar).
If the unit does not work and error 121 pops up as the active error the unit is faulty, contact your dealer for a replacement. If the error is only present in the history data and the unit operates normally this error can be ignored safely. Explanation: when the unit powers up for the very first time in the factory, it does not have calibration data and an error 121 is logged. Obviously this should have been cleared, but in the beginning units left the factory with this message still in the history data.
The unit performs internal diagnostics when activating its internal DC-DC converter. This error indicates that something is wrong with the DC-DC converter.
This error will not auto-reset. Check the installation and restart the unit using the power-switch. If the error persists the unit is probably faulty.
Internal DC voltage measurement error, is raised in case an internal (high-) voltage measurement does not match certain criteria. And it means that a measurement circuit inside the unit is broken.
Make sure to update the firmware to at least v1.08, in previous firmwares the limits were too strict. And it could trigger falsely during MPPT start-up in the morning and MPPT shutdown in the evening.
The unit might have seemingly worked fine before the firmware update; but it is really broken, not safe for use, and if it hadn't stopped working already then it would have stopped working soon. Which is why we added this internal check.
This error will not auto-reset. Check the installation and restart the unit using the power-switch. If the error persists the unit is probably faulty and must be sent in for repair/replacement.
The unit performs internal diagnostics when activating its internal voltage supplies. This error indicates that something is wrong with an internal supply voltage.