MultiPlus-II 120V | 12/3000/120-50 | 24/3000/70-50 | 48/3000/35-50 | ||
PowerControl & PowerAssist | Yes | ||||
Transfer switch | 50A | ||||
Maximum AC input current | 50A | ||||
INVERTER | |||||
DC Input voltage range | 9.5 - 17V | 19 - 33V | 38 - 66V | ||
Output in inverter mode | Output voltage: 120VAC ± 2% Frequency: 60Hz ± 0.1% | ||||
Continuous output power at 25°C (2) | 3000VA | ||||
Continuous output power at 25°C | 2400W | ||||
Continuous output power at 40°C | 2200W | ||||
Continuous output power at 65°C | 1700W | ||||
Peak power | 5500W | ||||
Maximum efficiency | 93% | 94% | 95% | ||
Zero load power | 13W | 13W | 11W | ||
Zero load power in AES mode | 9W | 9W | 7W | ||
Zero load power in Search mode | 3W | 3W | 2W | ||
CHARGER | |||||
AC Input | Single phase: 90-140VAC 45 - 65Hz | ||||
Charge voltage 'absorption' | 14.4V | 28.8V | 57.6V | ||
Charge voltage 'float' | 13.8V | 27.6V | 55.2V | ||
Storage mode | 13.2V | 26.4V | 52.8V | ||
Maximum battery charge current (3) | 120A | 70A | 35A | ||
Battery temperature sensor | Yes | ||||
GENERAL | |||||
Auxiliary output (4) | 32A | ||||
External AC current sensor (optional) | 100A | ||||
Programmable relay (5) | Yes | ||||
Protection (1) | a - g | ||||
VE.Bus communication port | For parallel, split phase and three phase operation, remote monitoring and system integration | ||||
General purpose com. port (6) | Yes, 2x | ||||
Remote on-off | Yes | ||||
Ambient temperature range | -40 to +65°C (-40 - 150°F) fan assisted cooling | ||||
Maximum humidity (non-condensing) | 95% | ||||
ENCLOSURE | |||||
Material & Colour | Steel, blue RAL 5012 | ||||
Protection category | IP21 | ||||
Battery-connection | M8 bolts | ||||
120 VAC connection | Screw terminals 13mm² (6 AWG) | ||||
Weight | 29 kg (64 lb) | ||||
Dimensions hxwxd | 578 x 277 x 148 mm 22.7 x 10.9 x 5.8 inch | 536 x 277 x 147 mm 21.1 x 10.9 x 5.8 inch | 572 x 277 x 147 mm 22.5 x 10.9 x 5.8 inch | ||
STANDARDS | |||||
Listing | UL 458 | UL 458 | UL1741 | ||
Safety | EN-IEC 60335-1, EN-IEC 60335-2-29, CSA 22.2 107.1-16 | ||||
Emission, Immunity | EN 55014-1, EN 55014-2 EN-IEC 61000-3-2, EN-IEC 61000-3-3 IEC 61000-6-1, IEC 61000-6-2, IEC 61000-6-3 | ||||
MultiPlus-II 120V | 24/5000/120-95 | 48/5000/70-95 | ||
Transfer switch | 95A | |||
Maximum AC input current | 95A | |||
INVERTER | ||||
DC Input voltage range | 19 - 33V | 48V | ||
Output in inverter mode | Output voltage: 120VAC ± 2% Frequency: 60Hz ± 0,1% | |||
Continuous output power at 25°C (2) | 5000VA | |||
Continuous output power at 25°C | 4000VA | |||
Continuous output power at 40°C | 3700VA | |||
Continuous output power at 65°C | 3000VA | |||
Peak power | 9000VA | |||
Maximum efficiency | 95% | 96% | ||
Zero load power | 24W | 19W | ||
Zero load power in AES mode | 10W | 10W | ||
Zero load power in Search mode | 3W | 3W | ||
CHARGER | ||||
AC Input | Single phase: 90-140VAC 45-65Hz | |||
Charge voltage 'absorption' | 28.8V | 57.6V | ||
Charge voltage 'float' | 27.6V | 55.2V | ||
Storage mode | 26.4V | 52.8V | ||
Maximum battery charge current (3) | 95A | 70A | ||
GENERAL | ||||
Auxiliary output (4) | 43A | 48A | ||
Protection (1) | a – g | |||
Pollution Degree (PD) & Overvoltage Category (OVC) | PD: 2 & OVC III | |||
Ambient temperature range | -40 to +60°C (-40 - 140°F) fan assisted cooling | |||
Humidity (non-condensing) | max 95% | |||
ENCLOSURE | ||||
Battery-connection | 2x M8 bolts | |||
120 VAC connection | 35mm2 (2 AWG) | |||
Weight | 29 kg (64 lb) | 32 kg (70 lb) | ||
Dimensions hxwxd | 627 x 350 x 150 mm 4.7x13.8x5.9 inch | 676x329x164 mm 26.6 x 13.0 x 6.5 inch | ||
STANDARDS | ||||
Listings | - | UL1741 | ||